正压送风风机出口处是否应加装防火阀

请教一下几位老师,正压送风风机出口处是否应加装防火阀

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

李中良 24-12-17

防火阀安装一般安装在需要进行防火分隔处,正压送风机向室内需要正压的场所送风,不存在回燃的问题,规范没讲此处要装防火阀。

0 0 [回复]举报

小卡了米   回复: 李中良24-12-18

谢谢老师,我看图集上有,但是又没找到联动关系,所以不知道应该不应该安装这个70度防火阀

0 0 [回复]举报

EHS专家-DL 25-03-24

根据《建筑防火设计规范》及相关技术标准,‌加压送风管穿越防火分隔处无需设置防火阀‌,其安全性通过耐火风管(≥1h)和封闭式风井实现‌。因而正压送风风机出口处不加装防火阀,反而加装后会引起阀门误动作关闭,中断送风,影响疏散安全‌,加系统漏风率和阻力,降低送风效率‌等。

0 0 [回复]举报

小卡了米   回复: EHS专家-DL25-03-25

谢谢您

0 0 [回复]举报

潘天坤 25-05-12

不知道楼主说的是出口还是入口,加压送风的入口一般是排出室外处,此时如果管道没有穿越防火隔墙(

建筑外墙一般不属于防火隔墙)可以不需要设置防火阀

是否设置防火阀,要看是否穿防火隔墙(包括楼板和风井处)

例如墙上设置加压送风口,此情况需要设置防火阀

例如前室或者楼梯间顶部设置加压送风口,此时风管穿越防火隔墙的区域需要设置防火阀

1 0 [回复]举报

小卡了米   回复: 潘天坤25-05-12

谢谢,您解释的最清楚

0 0 [回复]举报