隔膜式报警阀组手动复位球阀保持常开还是常闭

隔膜式预作用报警阀组其手动复位球阀保持常开还是常闭?请教各位大佬和老师

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

空中 25-04-17

预作用的可以参考雨淋阀组的复位方式

隔膜室控制阀关闭(应常开),

复位球阀关闭(复位时应打开,复位后应关闭)



0 0 [回复]举报

李勤 25-04-18

复位法应该常闭,要不电磁阀开启时左下侧的细管中的水会六道电磁阀,影响中间隔膜压力降低时间,从而影响报警阀开启时间

0 0 [回复]举报