消防问答 > 气体灭火 提问

关于七氟丙烷气体灭火系统喷头布置问题

七氟丙烷气体灭火系统喷头布置采用下喷距防护区顶面距离超500 mm,后改上喷布置后喷头高于梁,且与梁的水平距离很近,是否影响气体喷洒效果,规范上又没有提喷头与障碍物的距离要求,请问大家这种情况是否满足规范要求

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

EHS专家-DL 25-05-16

应该是不符合规范要求的,上喷与梁太近可能会因梁阻挡导致局部灭火剂浓度不足。为啥不整改成下喷距防护区顶面距离不超过500 mm这样就符合规范要求。

0 0 [回复]举报

消防资源网 25-05-16

气体灭火喷头常规都是下喷安装,距顶500mm不是强条,是谁要求上喷呢?

1 0 [回复]举报

消防资源网   回复: 消防资源网25-05-16

如果要求必须小于500mm,管道可以穿梁,或者贴梁,往上翻,再下来,保证500mm,但是这样会增大压力损失

0 0 [回复]举报

最新问题

关闭

关闭