消防问答 > 自喷灭火系统 提问

关于悬挂干粉灭火器能否视为悬挂干粉灭火装置,同时是否能够代替自喷灭火设施的疑问。

如题,悬挂干粉灭火器能否代替喷淋、气灭等设备作为场所的自喷灭火设施?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 11 回答

小唐12321 25-06-04

不能

0 0 [回复]举报

EHS专家-DL 25-06-04

悬挂干粉灭火器‌不能视为自动灭火装置‌,也‌不可替代喷淋或气体灭火系统‌作为场所合规的自喷设施。其定位属于固定式灭火器,仅适用于规范未强制设置自喷系统的局部小范围防护,或作为辅助措施

0 0 [回复]举报

牛疼   回复: EHS专家-DL25-06-04

您说的局部小范围是指的大概哪些?类似于小型IT机房这种么?

0 0 [回复]举报

李勤 25-06-04

0 0 [回复]举报

阿龙 25-06-04

部分小型场所里,接了控制线的可以,没接线的不能参与联动的不行。

0 0 [回复]举报

牛疼   回复: 阿龙25-06-05

就是单独的吊装干粉灭火器

0 0 [回复]举报

牛丫头消防课堂 25-06-05

首先,你说的悬挂式干粉灭火器,那么防护区就是全淹没灭火,你现在的悬挂式灭火器无法满足《消防设施通用规范》中关于干粉灭火系统的基本控制功能要求:

9.0.8 用于经常有人停留场所的局部应用干粉灭火系统应具有手动控制和机械应急操作的启动方式,其他情况的全淹没和局部应用干粉灭火系统均应具有自动控制、手动控制和机械应急操作的启动方式。

0 0 [回复]举报

牛疼   回复: 牛丫头消防课堂25-06-05

主要是针对小型IT机房的自喷设施的设置有此一问,能否用吊装干粉灭火器代替自喷设施。

0 0 [回复]举报

牛丫头消防课堂   回复: 牛疼25-06-05

严格来讲,不合适

0 0 [回复]举报

牛丫头消防课堂   回复: 牛疼25-06-05

温控+电控的话,可以作为自动灭火

1 0 [回复]举报

牛疼   回复: 牛丫头消防课堂25-06-06

谢谢了,我也认为单独的装置只是某系统的配件,不能代替成套的消防设施。

1 0 [回复]举报