消防问答 > 消防给排水 提问

消防水泵的连锁启动

消防水泵的连锁启动,水泵控制柜的手自动设置是否有影响?


请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 8 回答

陈曲 23-04-20

必须自动状态

0 0 [回复]举报

小工程师 23-04-20

必须在自动状态,连锁起泵,手动状态顾名思义也算是对水泵的一种保护,当你检修水泵的时候,手动状态就可以避免一些问题,当你在自动状态的时候,手动优先,这是题外话

0 0 [回复]举报

  回复: 小工程师23-04-21

那是不是可以理解为连锁控制的控制回路是需要经过控制柜的,经过控制柜的手自动开关再给动作信号给水泵?我前面理解成连锁是直接控制消防水泵的启动,没有经过控制柜。

0 0 [回复]举报

小工程师   回复: 23-04-23

是的 啊 肯定要经过控制柜,你打开控制柜或者看看二次接线图纸就明白了,转换开关,直启,连锁启动,主机启动,都是由不同的线路组成的,这些线路集成在控制柜里面,没那么复杂,就是逻辑关系问题,到头来启动水泵的最后一关就是启动交流接触器KM,

0 0 [回复]举报

畅波 23-04-21

控制柜不在自动状态,没法连锁起动的

0 0 [回复]举报

消防老胡 23-04-21

       联锁启泵不应受配电控制柜控制回路的手自动状态影响。

       实际上无论哪个地方,工地或项目上99%的现场配电控制柜都被人为设置成了手动状态,如果现场配电控制柜时刻处于自动状态,联动启泵就可以了,规范还何来要求流量开关、压力开关和低压压力开关进行连锁启泵?什么现场维修过程中如果远程手动启动或者联锁启泵危机附近人员安全的话都是扯淡。

      根本的原因是我们的配电控制柜没有经过专业机构的强制认证,或者即使通过自愿认证的设备,认证机构检测人员专业水平受限,不能发现问题而已。

     在《民用建筑电气设计标准 GB51348-2019》第9.2.23条“交流电动机的控制回路设计应符合下列规定:……4 自动控制、联锁或远方控制的电动机,应有就地控制和解除远方控制的措施,当突然启动可能危及周围人员安全时,应在电动机旁装设启动预告信号和应急断电开关或自锁式按钮,对于自动控制或联锁控制的电动机,还应有手动控制和解除自动控制或联锁控制的措施”之规定。

要在控制柜装设启动预告信号和应急断电开关或自锁式按钮,对于自动控制或联锁控制的电动机,还应有手动控制和解除自动控制或联锁控制的措施。

0 0 [回复]举报

小工程师   回复: 消防老胡23-04-23

大部分的控制柜都在自动把,应该,我参加的维护检测项目的柜子都是自动,包括主机,不过人员密集场所的主机有24小时值班,都在手动,可以理解,但是水都在自动

0 0 [回复]举报

陈曲   回复: 消防老胡23-04-23

消火栓和喷淋规范这里写的是 不应受消防联动控制器处于自动或手动状态影响 所以连锁启动根本原因是为防止消控室的各种状况无法及时处置火情

0 0 [回复]举报

最新问题

关闭

关闭