排烟风管包裹采用离心玻璃棉是否可行?

排烟风管包裹采用离心玻璃棉是否可行?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 5 回答

我的是昵称 23-11-07

不可行。离心玻璃棉的工作温度在200℃以下,适合用在低温管道。 而排烟管道防火要达到1.5小时,温度在达到280度时排烟风机停止工作,而管道肯定是超过280度的。

1 0 [回复]举报

WeiHL   回复: 我的是昵称23-11-09

谢谢大佬

1 0 [回复]举报

whale 23-11-07

防火包裹可以参考22K311-5,附录一

0 0 [回复]举报

WeiHL   回复: whale23-11-09

谢谢大佬

0 0 [回复]举报

潘天坤 24-06-19

市面上离心玻璃棉产品一般燃烧性能不符合规范要求

同时此做法无通风管道耐火极限报告,耐火极限可能不符合规范要求

0 0 [回复]举报