消防问答 > 自喷灭火系统 提问

敞开式汽车库是否需要设置自动喷淋灭火系统

山东地区,一个停车楼,地下一层,地上四层,地下一层停车80个,地上停车位379个。地下一层是要做自动喷淋了。地上四层部分是否需要考虑设置自动喷淋灭火系统啊?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 2 回答

安洪全 24-02-02

建筑防火通用规范 GB55037-2022

8.1.10 除敞开式汽车库可不设置自动灭火设施外,I、Ⅱ、Ⅲ类地上汽车库,停车数大于10辆的地下或半地下汽车库,机械式汽车库,采用汽车专用升降机作汽车疏散出口的汽车库,I类的机动车修车库均应设自动灭火系统。

0 0 [回复]举报

颂潇颂潇 24-02-26

都敞开式了,顶都没有,管网怎么铺设?探头怎么安装?

0 0 [回复]举报