关于气体灭火剂用量的计算

根据规范公式,算出七氟丙烷的用量,是只需要这些用量吗?实际工程中需要在附加一些用量吗

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 3 回答

小女子 24-06-06

看设计图纸

0 0 [回复]举报

消防痞子 24-06-06

实际用量=设计用量+喷设后钢瓶内剩余量。一般加3kg或4kg,根据瓶组规格确定

0 0 [回复]举报

黄辉 24-06-07

以七氟丙烷灭火系为例:

存储量 = 设计用量+存储容器剩余量+管道剩余量


设计用量 按3.3.14-1计算得出。


存储容器剩余量,这个可以咨询厂家,也可以保守估算。具体可参考以下文章:

气体灭火系统钢瓶剩余量是怎么确定的?


管道剩余量,大多数情况下可以不计(3.3.14第5款),如果需要计算的时候,计算就比较复杂了,手工计算比较繁琐,一般用专用的设计软件计算。



0 0 [回复]举报