消防问答 > 自喷灭火系统 提问

预作用系统必须有充气设备吗?

我是单连锁,预作用阀组可以不加充气设备吗

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 7 回答

wetom 25-04-28

可以不充气单连锁

0 0 [回复]举报

花花世界的   回复: wetom25-04-28

有规范支撑吗

0 0 [回复]举报

wetom   回复: 花花世界的25-04-28

图集嘛

0 0 [回复]举报

消防资源网 25-04-28

0 0 [回复]举报

gss123 25-04-30

预作用空压机需要强制送检吗


0 0 [回复]举报

牛丫头消防课堂 25-05-01

有规范依据,《自动喷水灭火系统设计规范》 GB50084-2017,对比预作用和干式系统就知道,干式系统明确管网内有压气体;预作用仅仅是管网内不充水,也就是可以有气,也可以没气,如果充气,只是利用有压气体检测管道是否严密,看一下三个条款:

2.1.5 干式系统 :准工作状态时配水管道内充满用于启动系统的有压气体的闭式系统。

2.1.6 预作用系统  :准工作状态时配水管道内不充水,发生火灾时由火灾自动报警系统、充气管道上的压力开关联锁控制预作用装置和启动消防水泵,向配水管道供水的闭式系统。

5.0.17 利用有压气体作为系统启动介质的干式系统和预作用系统,其配水管道内的气压值应根据报警阀的技术性能确定;利用有压气体检测管道是否严密的预作用系统,配水管道内的气压值不宜小于0.03MPa,且不宜大于0.05MPa。

0 0 [回复]举报