水泵电动机功率

消防验收时,发现水泵电机的流量与扬程符合设计要求.电机功率设计要求是45KW,实测只有30KW.是不是要提出来,强制将水泵电机更换掉.

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 3 回答

永锅 22-10-25

消防验收首先是按审查合格的竣工图验收,图纸设计有缺陷的,按消防规范验收。

水泵功率没有按设计文件设置,是必须换掉的;

如果不换,建设单位可以和设计单位沟通变更图纸设计,报原审图机构审核,审核通过按设计图纸验收。

1 0 [回复]举报

波波老板   回复: 永锅22-10-28

非常感谢朋友的指点,受教啦!

0 0 [回复]举报

南明离火 22-10-29

技术先进,功率低 扬程和流量也能达标,这个不用换吧

0 0 [回复]举报