消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

室外自动喷水灭火系统需要设置水泵接合器吗

比如油浸式变压器的水喷雾系统、液态烃球罐的水喷雾等

appleba | 2024-11-02 21:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

张治福 2024-11-04 11:32 10 [回复]举报

是的,需要设置的。

5.4.2 自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统和固定消防炮灭火系统等水灭火系统,均应设置消防水泵接合器。

消防网友70233 2024-11-04 16:36 20 [回复]举报

室外的可以不设置,理由如下:

1.水喷雾灭火系统技术规范   5.4.1 室内设置的系统宜设置水泵接合器。

2.《建筑防火通用规范》  8.1.12 下列建筑应设置与室内消火栓等水灭火系统供水管网直接连接的消防水泵接合器,且消防水泵接合器应位于室外便于消防车向室内消防给水管网安全供水的位置:     1 设置自动喷水、水喷雾、泡沫或固定消防炮灭火系统的建筑;

条文解释:本条规定了应设置消防水泵接合器的建筑及其基本设置要求,以便消防车到场后能充分利用建筑物内的既有消防给水系统和水消防设施。消防水泵接合器主要用于连接消防车,并通过消防车加压向室内消火栓给水系统、自动喷水或水喷雾等水灭火系统或设施供水。

3.《消防给水及消火栓系统技术规范》 5.4.1 下列场所的室内消火栓给水系统应设置消防水泵接合器:    1 高层民用建筑;    2 设有消防给水的住宅、超过五层的其他多层民用建筑;    3 超过2层或建筑面积大于10000m2的地下或半地下建筑(室)、室内消火栓设计流量大于10L/s平战结合的人防工程;    4 高层工业建筑和超过四层的多层工业建筑;    5 城市交通隧道。 5.4.2 自动喷水灭火系统、水喷雾灭火系统、泡沫灭火系统和固定消防炮灭火系统等水灭火系统,均应设置消防水泵接合器。

条文解释:室内消防给水系统设置消防水泵接合器的目的是便于消防队员现场扑救火灾能充分利用建筑物内已经建成的水消防设施,一则可以充分利用建筑物内的自动水灭火设施,提高灭火效率,减少不必要的消防队员体力消耗;二则不必敷设水龙带,利用室内消火栓管网输送消火栓灭火用水,可以节省大量的时间,另外还可以减少水力阻力提高输水效率,以提高灭火效率;三则是北方寒冷地区冬季可有效减少消防车供水结冰的可能性。消防水泵接合器是水灭火系统的第三供水水源。


以上三本规范里,基本上可以看出,只室内设置的水喷雾系统需要设置水泵接合器。   户外布置的系统,消防车来了直接对着着火的地方喷射就行,没有必要把水输送到管道到水喷雾系统,如同脱裤子放屁,多此一举。

 

静楠   回复: 消防网友702332024-11-13 12:45

消防车来了喷出来的是直流水,而水喷雾系统喷出来的是雾,雾没有导电性,水有导电性,如果按你这么说,水能代替雾的作用,那直接上水炮和室外消火栓好了呀,为啥还要设水喷雾系统?水喷雾的灭火原理和直流水都不一样。

0    0 [回复]举报

关闭

关闭

手机APP下载