使用七氟丙烷气体灭火系统的配电室可以有人员内部办公吗

元亨 | 2024-11-10 16:29
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

张治福 2024-11-11 10:20 10 [回复]举报

可以,但不推荐。

很想说一句,配电室里面办公(值班),这企业也太那啥了,隔壁整个小值班室就不行么。

jinyanwu 2024-11-13 10:10 00 [回复]举报

我感觉应该是不能办公(值班),因为那个七氟丙烷还要“判断”里面是否有人值班,当火灾时,七氟丙烷根据火灾信号直接或者延时发个报警信号就喷发了。万一这个人睡岗了没有听到,谁来负责?所以最好的办法就是隔离出去。

同时配电室也存在电磁辐射,有职业伤害。

当然法规上(GB51348-2019)低压配电室可以设置值班室,只是值班部位距离配电装置应稍远一点,配电装置离墙3m: