请教:根据GB50974-2014第7.4.9条规定,多层和高层建筑的试验消火栓应设置在其屋顶。如果建筑的屋面是不上人屋面(仅留有上人人孔)或者工业建筑设置斜屋面,试验消火栓该设在哪里?

请教:根据GB50974-2014第7.4.9条规定,多层和高层建筑的试验消火栓应设置在其屋顶。如果建筑的屋面是不上人屋面(仅留有上人人孔)或者工业建筑设置斜屋面,试验消火栓该设在哪里?

xiaobaixh | 2024-12-17 11:00
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 2

LHH2737 2024-12-17 11:09 00 [回复]举报

设在最高层,比如总共4层,就把4层的某一个消火栓兼做试验消火栓

喧哗 2024-12-17 11:23 00 [回复]举报

选一个水力最不利点,设置试验消火栓,就算单层建筑也做试验消火栓