消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防泵的启停要求

消防电泵和柴油泵多久启停运行一次,每次运行时长是多少?或者有什么要求?

李斌0708 | 2025-02-03 09:13
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防工程师小郭 2025-02-05 09:23 10 [回复]举报

每月至少手动启停一次,每次不少于5分钟。

龙行天下的龙 2025-02-05 10:25 00 [回复]举报

前两天看到哪个规范要求半个月启动一次,我一般都是一个月启动一次,启动一下就停。

阿龙 2025-02-05 11:43 00 [回复]举报

根据《自动喷水灭火系统施工及验收规范》(GB50261-2017)9.0.4 消防水泵或内燃机驱动的消防水泵应每月启动运转一次。当消防水泵为自动控制启动时,应每月模拟自动控制的条件启动运转一次。

根据《消防给水及消火栓系统技术规范》(GB50974-2014)14.0.4 消防水泵和稳压泵等供水设施的维护管理应符合下列规定:
1 每月应手动启动消防水泵运转一次,并应检查供电电源的情况;
2 每周应模拟消防水泵自动控制的条件自动启动消防水泵运转一次,且应自动记录自动巡检情况,每月应检测记录;
3 每日应对稳压泵的停泵启泵压力和启泵次数等进行检查和记录运行情况;
4 每日应对柴油机消防水泵的启动电池的电量进行检测,每周应检查储油箱的储油量,每月应手动启动柴油机消防水泵运行一次;

综上消防水泵和柴油机消防水泵都是每月启动一次,正常启动几秒钟就行了,如果管网较大或者老化严重的话建议关闭出水管路阀门再测,要不然可能会跑水。

潘天坤 2025-02-05 13:52 00 [回复]举报

消水规GB50974有提到:每月应手动启动消防水泵运转一次;每周应模拟消防水泵自动控制的条件自动启动消防水泵运转一次,;每日应对柴油机消防水泵的启动电池的电量进行检测,每周应检查储油箱的储油量,每月应手动启动柴油机消防水泵运行一次



关闭

关闭

手机APP下载