消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

多层民用建筑需要设置配电室吗?

最近遇到1例开业检查不通过,因为没有设置配电室,规范却未查到相关条文。多层民建采用三级负荷是否有设置配电室的必要?

| 2025-04-02 20:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

小唐12321 2025-04-03 09:40 00 [回复]举报

细说具体

EHS专家-DL 2025-04-03 14:32 10 [回复]举报

  1. 负荷等级与配电室设置的直接关联性
    现行国家标准未明确要求三级负荷必须设置独立配电室,其设置必要性主要取决于建筑规模、用电设备分布及管理需求:

  2. 若建筑单体总用电量较小(如≤100kW)且供电半径合理(低压线路长度≤150m),可采用楼层配电箱或户外箱式变电站分散供电,无需设置专用配电室‌;当用电设备分散且维护需求较高时,集中设置配电室可提升管理便利性,但非强制性要求‌。
  3. 消防相关条款的间接影响
    根据《建筑防火通用规范》GB55037-2022第10.1.5条,消防用电设备需采用专用供电回路‌。若建筑包含消防设施(如应急照明、消火栓泵),即便整体负荷等级为三级,仍需确保消防回路独立性,此时设置配电室可优化线路管理‌。

  4. 处理建议

    1. 技术复核与整改路径

      • 委托设计单位出具用电负荷计算书,证明现有供电方案满足三级负荷要求且符合《民标》GB51348-2019关于分散供电的规定‌;若存在消防用电设备,需补充专用回路设计图纸,并通过增设防火分隔措施(如独立配电箱+耐火电缆)替代配电室功能‌。
    2. 与消防部门沟通要点

      • 提供《民标》GB51348-2019第3.2.10条等条文,说明三级负荷可采用非专用配电室的供电方式‌;引用《低压配电设计规范》GB50054-2011第4.2.1条,论证现有配电装置安装位置(如竖井、设备间)满足安全防护要求‌。


关闭

关闭

手机APP下载