消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

挡烟垂壁无法同时满足建筑规范和暖通规范情况怎么办

在一些项目实际情况中,挡烟垂壁高度问题,建筑和暖通无法同时满足,例如:室内吊顶完成高度2400(排烟、空调、新风、水电管线在吊顶内,实在无法提高)、暖通要求储烟仓500、也就是挡烟垂壁要做到500,2400-500=1900 又不满足 建筑规范要求疏散净高不低于2.1m,这种情况证明办。

死胖子 | 2025-04-07 16:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


精彩评论

LHH2737 2025-04-08 09:16

不改变吊顶的前提下,无解,应当优先满足建筑规范,净高不低于2.1m的要求

查看原文
回答 | 3

潘天坤 2025-04-07 17:07 00 [回复]举报

如果划分多个防烟分区这种情况,看看能否采用镂空率大于25%的镂空吊顶,或者设置门、墙体等形式

住宅新规定又提高了某些区域的要求呢

EHS专家-DL 2025-04-07 17:19 00 [回复]举报

1、将封闭式吊顶改为‌镂空吊顶‌(开孔率>25%),允许将吊顶内空间高度计入储烟仓厚度‌;

2、使用电动或柔性挡烟垂壁,火灾时自动下降至500mm储烟仓高度,非火灾状态下收起以保障净高2.1m‌;

3、仅在排烟口附近局部加深储烟仓(如扩大排烟口上方空间),其他区域维持挡烟垂壁高度与净高平衡‌。


以上提供三种思路,具体采用哪种方式,均应提前与消防验收部门协商‌。最终方案需确保符合《建筑防烟排烟系统技术标准》GB51251-2017第4.6.2条及《建筑防火通用规范》GB55037-2022第7.1.5条双重强制要求‌。

LHH2737 2025-04-08 09:16 00 [回复]举报

不改变吊顶的前提下,无解,应当优先满足建筑规范,净高不低于2.1m的要求

关闭

关闭

手机APP下载