网吧疏散问题

一个网吧审图说疏散距离不得超11.25米,审图说是按照房间内任一点至房间直通疏散走道的疏散门的直线距离,不应大于表5.5.17规定的袋形走道两侧或尽端的疏散门至最近安全出口的直线距离。网吧(歌舞娱乐)是按照9米+25%。但是我网吧有两个方向的疏散门,这个不能算作两个安全出口吗?
问题2:我如果网吧里面有包间,请问包间到包间出口门是11.25米的要求吗?那么包间的出口门到网吧的疏散门又是多少距离。

须尽欢 | 2025-04-14 18:46
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

消防网友68723 2025-04-15 10:06 00 [回复]举报

1、房间内任一点至房间直通疏散走道的疏散门的直线距离与疏散门到安全出口的距离不一样

2、包间内任一点到直通疏散走道的疏散门的距离不大于5.5.17表的规定

小唐12321   回复: 消防网友687232025-04-15 14:54

1,在哪个文件解读,最大距离怎么计算。

0    0 [回复]举报

单车恋人 2025-04-16 14:26 00 [回复]举报

按娱乐场所定义:单向11.25,双向31.25米