消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

探测器的信号线是用双绞线符合要求吗?

请问一下,各位专家,火灾自动报警系统中探测器的信号线是用双绞线铺设,是否符合要求,铺设时没有穿管直接铺设在桥架里,现在频繁报故障,报完后一两分钟就回复了,请问专家这是什么原因造成的。

和我飞翔 | 2025-06-09 11:56
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

李勤 2025-06-09 12:52 00 [回复]举报

双绞线符合要求(双绞线为了抗干扰),但是应穿管。

EHS专家-DL 2025-06-09 14:45 10 [回复]举报

要结合双绞线额定电压来综合判断。根据《火灾自动报警系统设计规范》(GB 50116—2013)第11.1.1条:火灾自动报警系统的传输线路和 50V 以下供电的控制线路,应采用电压等级不低于交流 300V/500V 的铜芯绝缘导线或铜芯电缆。采用交流 220V/380V 的供电和控制线路,应采用电压等级不低于交流450V/750V 的铜芯绝缘导线或铜芯电缆。

如RVS型双绞线的额定电压通常为 ‌300/300V‌(依据JB/T 8734.3-2016标准),无法满足消防系统的电压要求。

桥架内电缆虽可不穿管(常规情况),但需确保固定牢固且桥架无尖锐边缘。若桥架内强电电缆与弱电信号线未有效分隔,可能因挤压或磨损导致线缆绝缘层破损。另外信号线与强电线路同桥架敷设时,若未采用金属隔板分隔或屏蔽措施,强电产生的电磁场会干扰探测器信号传输,引发瞬时故障。信号线接头松动、接地电阻过大或单点接地失效,导致电位差波动,引发短暂通讯中断。桥架密封不严时,潮气侵入可能导致线缆绝缘电阻下降,产生瞬时短路或漏电。采用万用表检测线路绝缘电阻,重点检查接头、转接盒及探测器端子排的连通性试试。。。。。

牛丫头消防课堂 2025-06-09 16:47 00 [回复]举报

需要满足《消防设施通用规范 》GB55036-2022第12.0.16调的要求:

火灾自动报警系统的供电线路、消防联动控制线路应采用燃烧性能不低于B2级的耐火铜芯电线电缆,报警总线、消防应急广播和消防专用电话等传输线路应采用燃烧性能不低于B2级的铜芯电线电缆。

还要满足《火灾自动报警系统设计规范》 GB50116-2013第11.1.1条关于电压等级的要求:

火灾自动报警系统的传输线路和 50V 以下供电的控制线路,应采用电压等级不低于交流 300V/500V 的铜芯绝缘导线或铜芯电缆。采用交流 220V/380V 的供电和控制线路,应采用电压等级不低于交流450V/750V 的铜芯绝缘导线或铜芯电缆。

关闭

关闭

手机APP下载