消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟风机启停

按通规,任意防火阀停风机,那我一个防烟分区280度防火阀熔断后联动停风机以后,其他分区的排烟口开启后风机还会再启动吗?也就是说风机会因为火灾的蔓延重复启停吗?

消防网友62117 | 2025-06-12 17:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

罗马苏丹 2025-06-13 09:04 00 [回复]举报

如果是支管上的防火阀动作,其他防烟分区排烟口还是可以让风机再启动了;如果是主管就不行了。

Along Niusk 2025-06-13 09:09 00 [回复]举报

排烟系统,只有风机前端的是280的常开防火阀,动作后联锁关闭风机 其它的烟口、跨区都是70度。 烟口常闭,手动或联动后开启 跨区常开,管道超温后关闭

把这个逻辑搞清楚了,就就会发现,你的问题本身就是个问题

火都烧到风机了,肯定要停风机,停了风机以后,其它的排烟口打开了也不会有什么影响,因为没有负压了就不会有气流了。管道内到了70度自己判断

牛丫头消防课堂 2025-06-13 09:13 20 [回复]举报

关于这个问题,去年我在第二届防火大会上作的主题报告,这个规范组的本意是:风机入口处的排烟防火阀直接连锁停止排烟风机;其他部位的排烟防火阀达到280度后自行关闭,并信号反馈参与与逻辑;当一套系统中全部排烟防火阀都达到了280度关闭后,由消防联动控制器联动停止相应的排烟风机。

小唐12321 2025-06-13 09:30 00 [回复]举报

想要就能达到,但是正常防烟分区280不能关闭风机,我觉得规范不合理。只能风机入口那个才能停

潘天坤 2025-06-13 10:15 00 [回复]举报

要看控制逻辑是怎么做的


已知只是做简单的联动逻辑,不复位的话风机不能二次启动,包括其他防烟分区确认火灾也启动不了

规范没有做太多的说明,目前做法满足规范要求即可


最后讲下,规范是几个位置联锁要求,还是所有位置都要联锁,存在一定争议。穿越防火隔墙不一定在规范几个设置要求里,这种情况是否要联锁不好判断

李勤 2025-06-13 15:04 00 [回复]举报

关闭

关闭

手机APP下载