自动喷水灭火系统喷头喷水压力问题

自动灭火系统是越低的层喷头压力越大,越高的层喷头压力越小吗?(前提:满足设计要求≥0.05mpa)

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

罗马苏丹 2025-06-15 20:55 10 [回复]举报

是的

牛丫头消防课堂 2025-06-15 23:38 10 [回复]举报

从压力分布是这样的,但是与采用的管径有关,多数设计会在不同楼层设置不同的减压孔板;

再就是根据供水压力采取减压阀等减压措施。

所以工程中高处的压力不一定低,低处的压力不一定高,具体看看采取了哪些减压措施。

李勤 2025-06-16 08:09 10 [回复]举报

小唐12321 2025-06-16 08:18 10 [回复]举报

同一个报警阀,未设置减压阀,就是差别在高度压差

EHS专家-DL 2025-06-16 11:20 10 [回复]举报

低楼层喷头压力普遍高于高楼层‌,这是由重力供水特性决定的物理规律。