复合防火风管法兰与风管连接方式

复合防火风管制作风管与法兰连接方式能否采用自攻螺丝

笑场 | 2025-06-23 15:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

牛丫头消防课堂 2025-06-24 10:52 00 [回复]举报

在复合防火风管法兰连接中,‌严禁使用自攻螺丝‌,因其会破坏风管的防火密闭性和结构完整性,具体限制及替代方案如下:
 禁止使用自攻螺丝的关键原因
破坏密封性‌
自攻螺丝的穿透作用会导致风管本体出现孔洞,造成漏风隐患,违反风管严密性强制规范。
防火风管需保证无泄漏(尤其防排烟系统),任何钻孔均会降低系统有效性。
违反防火规范‌
耐火极限≥1小时的风管要求本体及连接处均为不燃材料且结构连续,自攻螺丝的金属导热性可能形成“冷桥”,破坏整体防火性能。
穿越防火分隔时,钻孔会削弱风管耐火极限,不符合GB51251-2017要求。

合规替代方案
法兰连接方式‌
金属法兰‌:采用角钢法兰,螺栓按十字交叉顺序均匀紧固,法兰间加装耐火密封垫(如4mm厚石棉胶垫)。
复合材料法兰‌:使用PVC或铝合金专用法兰件,通过黏结剂与风管粘接,无需钻孔。
保温/防火层固定‌
保温钉焊接‌:优先采用焊钉固定保温材料,确保不穿透风管内壁。
黏结固定‌:使用耐高温胶粘剂粘贴保温层,接触面需清洁并满涂胶粘剂。
加固要求‌
边长≥1600mm的中高压风管,应采用角钢外加固框,通过焊接或螺栓与法兰连接。
加固件不得直接穿透风管壁,需通过法兰或外挂支架传递受力。
⚠️ 特殊场景注意事项
钢板面层复合风管‌:若设计允许钢板外露,可有限使用自攻螺丝固定外覆角钢(间距≤120mm),但螺丝仅限连接外部加固件,严禁穿透风管保温层及内壁,且需在钻孔处补涂密封胶。
低压非防火系统‌:普通通风风管在无耐火要求时,可严格按规范控制自攻螺丝使用(如间距、密封处理),但仍需优先选用无损连接。


牛丫头个人理解:防火风管系统的核心是保障结构连续性与密封性,自攻螺丝因物理破坏特性被主流规范禁止。实际施工需按系统压力等级及耐火要求,选择法兰等连接方式。


工程中,风管连接质量不尽人意。

潘天坤 2025-06-26 10:10 00 [回复]举报

是用于排烟系统嘛?

规范有要求矩形风管法兰的四角部位应设有螺孔,也有金属矩形风管螺栓孔距要求,综合起来就是应设置螺栓,并且有间距要求,自攻螺丝不属于螺栓,使用螺丝的话无法满足规范要求