消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

不设挡烟垂壁时的储烟仓厚度如何计算

防排烟规范4.2.4条,空间净高大于9m时,可不设挡烟垂壁,这时的储烟仓厚度如何计算

消防网友68723 | 2021-09-27 10:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

刘丽波 2021-09-29 10:37 00 [回复]举报

按你的实际需要正常设置,只是不加实际的挡烟设施。

一片冰雨 2021-09-29 20:54 00 [回复]举报

4.6.2 当采用自然排烟方式时,储烟仓的厚度不应小于空间净高的20%,且不应小于500mm;当采用机械排烟方式时,不应小于空间净高的10%,且不应小于500mm。同时储烟仓底部距地面的高度应大于安全疏散所需的最小清晰高度,最小清晰高度应按本标准第4.6.9条的规定计算确定。

消防网友68723   回复: 一片冰雨2021-09-30 09:03

不设挡烟垂壁,储烟仓厚度从何处计算

0    0 [回复]举报

一片冰雨 2021-09-30 23:18 10 [回复]举报

你应该想一下储烟仓设置的目的来考虑问题,设置储烟仓是为了在排烟设施起作用之前:一方面减少高温烟气的扩散速度,另一方面也是为了保证人员疏散的最低清晰高度;当高度大于9m的时候,这两个方面的问题都得到了解决,所以这个时候你设置挡烟垂壁的必要性就没有了;另外,你要纠结计算这个高度准备做什么呢?验收时会检查还是设计图上要求你标注高度吗?

消防网友68723   回复: 一片冰雨2021-10-01 09:58

设计图上一方面说无实体设挡烟垂壁,同时又说了储烟仓厚度,怎么理解

0    0 [回复]举报

潘天坤 2024-07-05 19:48 00 [回复]举报

这种情况,储烟仓厚度是根据设计清晰高度来的

虚拟挡烟垂壁没有实物,那么设计清晰高度满足最小清晰高度即可,当然也可以提高要求

例如空间净高大于10米的场所,最小清晰高度为1.6+1=2.6,此时如果设清晰高度为2.6米,则储烟仓厚度为10-2.6=7.4米。设计清晰高度也可以取5米,此时储烟仓厚度为5米,保证自然排烟方式储烟仓厚度不低于净高20%,机械排烟方式储烟仓厚度不低于净高10%即可


关闭

关闭

手机APP下载