厂房内房间的安全疏散

关于厂房内的某间房子,是否要设两个疏散门,依据什么

消防网友68723 | 2021-11-12 16:42
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

小马 2021-11-12 17:52 00 [回复]举报

3.7.1 厂房的安全出口应分散布置。每个防火分区或一个防火分区的每个楼层,其相邻2个安全出口最近边缘之间的水平距离不应小于5m。

消防网友68723   回复: 小马2021-11-15 09:19

我问的是,厂房内的某间房子,是否要设两个疏散门,依据什么

0    0 [回复]举报

hbedsn   回复: 消防网友687232021-11-16 17:19


配电间长度大于7m;电子设备间100m2;一般库房100m2;普通房间120m2;办公室按民用建筑处理;

0    0 [回复]举报