一层的歌舞娱乐场所,有一个包间的建筑面积超过100平米,那么设置排烟设施是应该所有包间和走道都设置,还是只针对这个100平米的包间设置排烟设施即可

浩波 | 2021-12-30 21:31
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

刘丽波 2021-12-31 11:14 30 [回复]举报

这个大于100平的房间需要排烟,走道是否排烟看长度是否超过20米,其他房间是否排烟看是否有建规8.5.4的情况存在。哪个部位需要排烟就设置哪里。

消防网友52694   回复: 刘丽波2022-01-24 15:44

走道小于20米是不是就不需要设置排烟(包括自然排烟和机械排烟)

0    0 [回复]举报

刘丽波   回复: 消防网友526942022-01-24 22:31

是的。

0    0 [回复]举报

GANSTER 2022-02-10 14:25 10 [回复]举报

设在一~三层的娱乐场所排烟大致有以下几种情况:1.大于100平米的包间考虑排烟;2.走道长度超过20米考虑排烟;3.无窗房间总面积大于200平米,单个房间面积不超50平米,与之关联的走道无论多长都要考虑排烟(或者各房间设排烟则走道不超20米时可以不考虑排烟);大于50平米的无窗房间考虑排烟。

潘天坤 2024-07-05 18:59 00 [回复]举报

建筑面积超过100平米的包间需要设置排烟设施,且不能通过与房间相同的公共走道排烟,此房间可以设置自然排,也可以设置机械排烟,满足规范要求即可

走道是否需要设置排烟,需要看走道是否满足排烟设防要求,如果属于需要设置排烟的走道,那么走道也需要设置排烟

最后就是是否存在其他需要设置排烟设施的区域,得看楼主补充信息了,暂时不知还存在什么其他区域