老师您好,主泵独立,系统有水炮,自喷,消火栓,在屋顶合用稳压泵,求详细分析一下能不能合用稳压泵,规范和图集都没有

浩波 | 2022-02-14 10:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

刘丽波 2022-02-14 13:17 20 [回复]举报

可以合用高位水箱,稳压泵需要独立设置,尤其是水炮,平时维持系统的压力较大,很难合用。图集上合用稳压泵的情况是消防主水泵也合用,要不然启各主泵压力不好确定。具体启主泵压力可以根据17s205总说明计算实例确定。