消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

有关联排商住楼室内消火栓系统设置疑问

首层商业网点平面图

二层及以上住宅平面图

老师您好,想请教联排商住楼室内栓设置疑问,希望得到释疑,谢谢。

工程概况:联排商住楼,每户占地7.8米❌14米,共21户联排,总长163.8米。地下2层,为共用汽车库,地上5层,建筑高度20米。首层为商业网点,2层以上为住宅,首层及以上户间完全分隔,各户自有一步疏散楼梯。联排建筑总体积约40000立方米。

疑惑:1、地下共有车库设有室内栓、自喷,首层各商业网点是否需要设置消火栓系统?2层及以上各户住宅部分是否需要设置室内栓?是否需要每层均设置?

2、建筑高度为20米,是否需要设置高位水箱?


设计学生 | 2022-11-12 01:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

充楞装傻 2022-11-12 10:40 00 [回复]举报

1、都可以不设消火栓,大于200要设卷盘。 鉴于车库有基础设施,建议住宅也配上。

2、水箱18吨,是多层公建-车库需要配备的。

设计学生   回复: 充楞装傻2022-11-18 11:07

谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载