感烟探测器距离距离回风口的距离是多少

感烟探测器距离空调回风口的距离是多少,有要求吗

冷风 | 2023-02-17 18:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

无花果 2023-02-17 18:48 10 [回复]举报

 火灾自动报警系统设计规范 GB50116-2013

6.2.8 点型探测器至空调送风口边的水平距离不应小于 1.5m ,并宜接近回风口安装。

规范只提到感烟探测器要远离送风口,对空调回风口的距离并未做要求。

张牙舞爪的张 2023-02-18 08:00 00 [回复]举报

0.5米

王涛 2023-02-22 10:52 00 [回复]举报

6.2.5 点型探测器周围 0.5m 内,不应有遮挡物。

6.2.58点型探测器至空调送风口边的水平距离不应小于 1.5m ,并宜接近回风口安装。

规范是这样要求;个人理解可以就设置在0.5m就行。