挡烟垂壁

老师您好,还是那个健身会所,2500平方米,层高5米,我计算的挡烟垂壁的厚度是净高的10%,那就是0.5米,最小清晰度是1.6+0.1*5=2.1米,我的挡烟垂壁的高度就是在0.6到2.1米之间了,我的建筑原主梁有0.7和1.1米,那我可以直接使用梁就可以达到挡烟垂壁的高度了,我就可以不用再设置玻璃或则其他不然材料作为挡烟垂壁了吧。
豆豆龙 | 2023-05-16 17:07
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

无名之辈 2023-05-17 09:12 00 [回复]举报

按照你说的,可以直接使用梁作为挡烟垂壁,当然前提是可以完全按照现有的梁来划分防烟分区。唯一需要注意的是需要复核储烟仓内有效的排烟口(窗)面积是否符合规范要求,如果不符合,则不能作为挡烟垂壁。

GANSTER 2023-05-17 09:27 00 [回复]举报

能否使用土建梁,首先取决于你是建筑专业还是暖通专业,假如是建筑专业你直接问跟你搭档的暖通专业,假如是暖通专业,这个问题就取决于你自己的排烟设计了。

消防网友78337 2023-05-17 15:06 00 [回复]举报

机械排烟口或自然排烟窗需要在储烟仓内,


储烟仓是由墙壁楼板(顶板)及挡烟垂壁围起来的空间。


或者你可以这样理解:

一盆水,你需要水自己流走,或者被抽走,就需要在水盆底开个洞,或者把吸水管放到水面以下。

储烟仓就是一个倒扣过来装烟的大盆子。

同同不同 2023-06-13 08:23 00 [回复]举报

储烟仓厚度:机排10%H,且不小于500,自然排20%H,且不小于500 ,尚应计算储烟仓内的排烟量

DZ王 2023-07-07 13:35 00 [回复]举报

挡烟垂壁要下垂至排烟口底部