消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

在厂房内的一个房间,是否可以不要门,只留门洞供通行?

在一个6000平的防火分区内,有一个1000平的房间,这个房间一共3个门,现在想取消门,只留门洞,是否可行。(6000平的防火分区内一共有三个小区域,这三个区域的火灾危险性类别都一样)

Charlie | 2023-06-27 09:30
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 10

安洪全 2023-06-27 11:08 00 [回复]举报

同一防火分区内墙都可以不设,不加门可以。

Charlie   回复: 安洪全2023-06-27 11:22

大佬有相关的标准条文可以佐证吗,非常感谢啊,我已在网上找了半天资源没结果了

0    0 [回复]举报

同同不同   回复: Charlie2023-06-27 13:01

勿须条文佐证,你看建规50016术语中的防火分区定义即可,若为同一防火分区或者同一防火单元,则不需设置防火墙或防火隔墙、楼板等防火分隔设施

0    0 [回复]举报

安洪全   回复: Charlie2023-06-27 13:06

这1000㎡的房间不是库房,不是辅助用房的话,就是没有分隔要求,所以找不到依据也是正常的。


0    0 [回复]举报

Charlie   回复: 同同不同2023-06-27 13:47

好的, 非常感谢

0    0 [回复]举报

Charlie   回复: 安洪全2023-06-27 13:47

好的好的,感谢大佬

0    0 [回复]举报

XF119 2023-06-27 13:42 10 [回复]举报

先看厂房建筑类别和火灾危险性等级,再看房间使用性质

Charlie   回复: XF1192023-06-27 13:49

大佬好,丙二类,房间的话也就是摆设备使用,只是工序不同管理部门不同,所以用墙分开,但又不想装门,只留门洞

0    0 [回复]举报

消防君 2023-06-27 17:39 00 [回复]举报

使用性质如果相同,防火分区面积符合要求,可以不设门。如果生产内容或使用性质不一样,视火灾危险性情况,才需要进行防火分隔(防火隔墙和防火门)

Charlie   回复: 消防君2023-06-28 09:10

好的,感谢大佬

0    0 [回复]举报

关闭

关闭

手机APP下载