消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防电梯前室和楼梯间前室能否合用一台加压风机?

同一个楼梯,在负一层对着独立前室,在负二层对着消防电梯前室,请问这两种前室能否合用一台加压风机?

飞云 | 2023-07-05 16:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

同同不同 2023-07-05 18:47 00 [回复]举报

图纸发来大家讨论一下,消梯未在负一层停靠?建筑图为什么会有这种情况?

飞云   回复: 同同不同2023-07-06 11:43

0    0 [回复]举报

同同不同 2023-07-07 06:53 10 [回复]举报

应该是不允许,应按照图纸在前室、合用前室楼梯间分别设置加压系统

潘天坤 2024-06-21 16:54 00 [回复]举报

独立前室和共用前室,两个不同的区域,一般无法共用

规范里没有提到前室共用,所以同一位置的前室应该没有限制,注意联动逻辑即可

楼梯间共用有一些前提条件,烟规51251有提到:地下部分为汽车库或设备用房时,楼梯间可共用机械加压送风系统。 如果地下部分不是汽车库或者设备用房的时候,不能合用。

地上和地下共用机械加压送风系统,应: 分别计算地上、地下部分的加压送风量,相加后作为共用加压送风系统风量。 采取有效措施分别满足地上、地下部分的送风量的要求。

关闭

关闭

手机APP下载