消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

走道排烟疑问

如平面图所示,现因走道宽度大于2.5m,应当设置2个防烟分区。根据《排烟规》表4.6.3注第3款的规定,因为有挡烟垂壁的分隔,防烟分区二是否已经不满足两端各有2个平方的排烟窗要求?

澜沐 | 2023-08-02 10:16
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

同同不同 2023-08-02 13:52 00 [回复]举报

有文说防烟分区两端必须2㎡么?那是烟规仅走廊需要排烟走廊两端吧?

陈曲 2023-08-03 07:40 00 [回复]举报

C3≥2㎡就行了

无名之辈 2023-08-03 13:45 00 [回复]举报

如果仅走道排烟,那就应该每个防烟分区都要满足两端2㎡排烟窗要求,且排烟窗间距不小于走道长度的2/3,个人理解

whale 2023-08-04 10:03 00 [回复]举报

C3满足防烟分区面积的2%且实验室八设置有排烟窗(储烟仓以内建筑面积2%)

潘天坤 2024-06-21 10:20 00 [回复]举报

要分为几种情况:

1、功能房间满足排烟要求,那么走道满足空间净高二分之一以上设置建筑面积2%自然排烟口即可

2、功能房间如果满足排烟要求,那么每个走道每个防烟分区都要具备两侧各2平方米自然排烟口且间距不小于走道长度的2/3

茶水间、文印室、卫生间是否要考虑排烟,这个有一定争议,这边不展开讨论

上述为根据国家规范的个人理解,有些地区技术文明可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑

关闭

关闭

手机APP下载