自然排烟可开启窗满足面积要求时,是否需要火灾时自动打开?

自然排烟可开启窗满足面积要求时,是否需要火灾时自动打开?如果不能自动打开也无法排烟作用呀?谢谢

zhouzhou | 2021-01-02 22:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2021-01-03 08:40 20 [回复]举报

《烟规》4.3.6 自然排烟窗(口)应设置手动开启装置,设置在高位不便于直接开启的自然排烟窗(口),应设置距地面高度1.3m〜1.5 m的手动开启装置。净空高度大于9m的中庭、建筑面积大于2000m2的营业厅、展览厅、多功能厅等场所,尚应设置集中手动开启装置和自动开启设施。

此条款自然排烟窗大部分仅要求设置手动开启装置。对于净空高度大于9m的中庭、建筑面积大于2000m2的营业厅、展览厅、多功能厅等场所,尚应设置集中手动开启装置和自动开启设施。 其他做法看一下《烟规》图示,4.3.6

 关于自动排烟窗可以看一下石老师专题 :探讨:自动排烟窗-控制方式.应用场所!

                                                               再议:常开防火门.自动排烟窗的温控自释放功能!

刘丽波 2021-01-03 09:23 40 [回复]举报