消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地下室分多个防火分区时,考虑空间利用率,消防补风是否可以多个防火分区共用一台消防补风风机?

根据规范:当建筑的机械排烟系统沿水平方向布置时,每个防火分区的机械排烟系统应独立设置。那么消防补风系统可否按最大排烟风机风量的50%以上设计?多个防火分区共用一台消防补风机,穿越防火分区的管道处加70度防火阀,每个防火分区的排烟风机均联动此补风机启动,是否可行?

涵涵 | 2023-12-17 11:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

GANSTER 2023-12-18 08:47 00 [回复]举报

没有什么不可以的

whale 2023-12-18 09:06 00 [回复]举报

不能,

涵涵   回复: whale2023-12-18 11:27

依据什么呢?

0    0 [回复]举报

whale   回复: 涵涵2023-12-19 09:34

没有明确条文啊,现在的消防各地要求都不一样

我们这边这么做蓝审直接PASS公司内审都过不去。如果补风风机和排烟风机一一对应,跨防火分区补风是可以的。多个防火分区共用一个我们这边不让做。

0    0 [回复]举报

涵涵   回复: whale2023-12-21 09:19

好的,谢谢

0    0 [回复]举报

关闭

关闭

手机APP下载