请教各位老师,什么情况下喷淋系统用减压阀组?谢谢了

请教各位老师,什么情况下喷淋系统用减压阀组?谢谢了

小卡了米 | 2024-03-01 13:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2024-03-04 13:01 00 [回复]举报

当管网、管件处超压了,就需要设减压设施。

比如报警阀组处,喷头处的工作压力大于了设计压力,需要做减压装置。

小卡了米   回复: 安洪全2024-03-14 11:53

谢谢老师,有没有实例能参考一下吗?

0    0 [回复]举报

安洪全   回复: 小卡了米2024-03-14 15:39

如:

建筑设计防火规范 GB50016-2014(2018年版)

12.2.2 消防给水系统的设置应符合下列规定:6 管道内的消防供水压力应保证用水量达到最大时,最不利点处的水枪充实水柱不小于10.0m。消火栓栓口处的出水压力大于0.5MPa时,应设置减压设施。


消防给水及消火栓系统技术规范 GB50974-2014

6.2.1 符合下列条件时,消防给水系统应分区供水:     1 系统工作压力大于2.40MPa;     2 消火栓栓口处静压大于1.0MPa;      3 自动水灭火系统报警阀处的工作压力大于1.60MPa或喷头处的工作压力大于1.20MPa。


6.2.2 分区供水形式应根据系统压力、建筑特征,经技术经济和安全可靠性等综合因素确定,可采用消防水泵并行或串联、减压水箱和减压阀减压的形式,但当系统的工作压力大于2.40MPa时,应采用消防水泵串联或减压水箱分区供水形式。



0    0 [回复]举报

小卡了米   回复: 安洪全2024-03-15 11:45

多谢多谢,学习了

0    0 [回复]举报