消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

预作用系统末端试水装置是如何测试的?

预作用糸统末端试水装置是如何测试的?

易学 | 2024-03-15 16:07
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

麻溜点 2024-03-19 17:08 00 [回复]举报

预作用的系统管道里面是有压气体,不用试水装置,也没有办法测试。

同同不同 2024-03-26 07:04 00 [回复]举报

若为双连锁系统可采用报警系统联动加打开末端试水的操作,看是否在规定时间内出水及流量压力是否符合设计要求,若为单连锁系统可采用自动报警系统联动,看是否在规定时间内充水,充水完成可打开末端试水测试流量压力是否满足设计要求

梅有名 2024-03-30 16:52 10 [回复]举报

你找个有末端的防火分区打开末端,开双自,在这个防火分区触发两个烟感模拟火灾确认状态,在触发信号的过程中找个人在末端那等着,一旦声光报警或切非开始就打开秒表记时,120秒内末端出水了测试就成功,没出水测试失败。

易学   回复: 梅有名2024-04-01 10:24

你做过吗?

0    0 [回复]举报

梅有名   回复: 易学2024-04-04 10:13

经常做

0    0 [回复]举报

关闭

关闭

手机APP下载