关于气体灭火系统的喷嘴布置的问题

喷嘴布置间距最小可以是多少,可以布置的密一点吗,感觉布置的密一点可以更好的充满全室

zzyzy | 2024-06-02 21:11
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防网友68723 2024-06-03 10:12 00 [回复]举报

3 喷头安装高度小于1.5 m时,保护半径不宜大于4.5 m;
      4 喷头安装高度不小于1.5m时,保护半径不应大于7.5 m。
3.1.13 喷头宜贴近防护区顶面安装,距顶面的最大距离不宜大于0.5 m。

zzyzy   回复: 消防网友687232024-06-03 15:44

谢谢

0    0 [回复]举报

香.香 2024-06-03 13:00 00 [回复]举报

气体灭火系统对喷头的布置有高度和最大保护半径的要求。你所说的布置间距就和最大保护半径有关系,喷头布置越高喷洒时不易被遮挡,保护的面积就相较大一些,当喷头布置高度小于1.5米时,保护半径不宜大于4.5米,当喷头布置高度不小于1.5米时,保护半径不应大于7.5米

黄辉 2024-06-04 08:23 00 [回复]举报

可以适当密点,喷头布置密度大,灭火剂喷放更均匀。但相应的管道,喷头数量也会增加。

管道增加涉及到管道压力损失的增加,极端情况下可能导致压损计算通不过。

管道和喷头的增加也会增加工程造价。