消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

管路水力计算

在设计管段的时候,一个楼层的右边前室和左边的前室能否共用一个排烟风机

腻浩 | 2024-07-02 12:01
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


精彩评论

潘天坤 2024-07-02 18:46

是机械排烟还是机械加压送风,不同区域的机械加压送风系统一般不能共用风机

如果共用排烟风机,两台风机的风量等参数是否一致,同时要考虑截面尺寸是否符合排烟量要求

查看原文
回答 | 5

潘天坤 2024-07-02 18:46 10 [回复]举报

是机械排烟还是机械加压送风,不同区域的机械加压送风系统一般不能共用风机

如果共用排烟风机,两台风机的风量等参数是否一致,同时要考虑截面尺寸是否符合排烟量要求

腻浩   回复: 潘天坤2024-07-03 10:58

感谢

0    0 [回复]举报

消防网友68723 2024-07-03 10:51 00 [回复]举报

当建筑的机械排烟系统沿水平方向布置时,每个防火分区的机械排烟系统应独立设置。

南明离火 2024-07-03 17:41 10 [回复]举报

前室 只有送风机

GANSTER 2024-07-08 10:35 00 [回复]举报

排烟和加压送风的原理和适用场景都没搞清楚,现在的暖通设计门槛这么低吗?

关闭

关闭

手机APP下载