消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

如下图,末端喷头都必须要安装防晃支架吗?还是只有一个喷头且短于一定的长度就不需要?

领悟AAA | 2024-09-08 09:04
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

磊中 2024-09-09 08:26 21 [回复]举报

根据自动喷水灭火系统施工及验收规范 GB50261-2017中5.1.15注3 管道支架、吊架的安装位置不应妨碍喷头的喷水效果;管道支架、吊架与喷头之间的距离不宜小于300mm;与末端喷头之间的距离不宜大于750mm

希望能帮到你

领悟AAA   回复: 磊中2024-09-09 23:37

所以,到底是要还是不要?

0    0 [回复]举报

磊中   回复: 领悟AAA2024-09-14 10:15

所以是要装支吊架的,距离喷头300mm-750mm之间

0    0 [回复]举报

LHH2737 2024-09-09 09:36 10 [回复]举报

每个DN25管道都需要一个防晃支架

消防网友68723 2024-09-09 11:16 10 [回复]举报

GB50261-2017,5.1.15, 5 当管道的公称直径等于或大于50mm时,每段配水干管或配水管设置防晃支架不应少于1个,且防晃支架的间距不宜大于15m;当管道改变方向时,应增设防晃支架。

关闭

关闭

手机APP下载