关于灭火器出厂满5年后不再需要每2年维修一次

消防设施通用规范 GB55036-2022前言中明确写明《建筑灭火器配置验收及检查规范》GB 50444-2008第5.3.2条废止,那么现有灭火器满5年后是不是可以不再按照每2年维修一次,只是对日常检查过程中发现损坏、失效等灭火器进行维修即可。

yoyo7887 | 2025-02-11 15:04
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 7

小唐12321 2025-02-11 15:34 00 [回复]举报

只是废止强制性

红门铠甲   回复: 小唐123212025-02-11 17:30

那到底是需要还是不需要!

0    0 [回复]举报

小唐12321   回复: 红门铠甲2025-02-12 08:05

新规范没出来就需要

0    0 [回复]举报

nekomiya 2025-02-12 11:57 00 [回复]举报

目前的要求是有定期维修,没有强制性。所以其实还是按照每两年一次合适毕竟不用动脑子另外想而且还有依据

小唐12321   回复: nekomiya2025-02-12 14:39

两年一次要钱啊


0    0 [回复]举报

nekomiya   回复: 小唐123212025-02-20 08:58

那就自己调定期是定多久咯又不是非得两年。不都说了不存在一定两年一检你可以设到三年一检甚至五年一检然后等报废咯。

0    0 [回复]举报

赖峰 2025-02-17 16:30 10 [回复]举报

规范《GB50444-2008》 第5.3.2 并未废除,只是在规范《消防设施通用规范》GB 55036-2022 前言明确同时废止下列工程建设标准相关强制性条文:《GB50444-2008》第5.3.2


《通用规范》实施后,相关工程建设标准中的强制性条文废止,配套衔接的相关标准正在修订中。在配套衔接的相关标准出台前,被废止的强制性条文,与《通用规范》要求一致的,可视为推荐性条文,作为落实《通用规范》的方法和措施。详见