消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请教一下各位大佬,建筑高度7.160 m, 体积7327立方米,单层丙类厂房,这个消火栓栓口动压取多少?

请教一下各位大佬,建筑高度7.160 m, 体积7327立方米,单层丙类厂房,这个消火栓栓口动压取多少?

QQ君 | 2025-03-28 09:44
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

EHS专家-DL 2025-03-28 10:20 00 [回复]举报

0.35MPa。

厂房类型:‌丙类厂房‌(火灾危险性分类)‌;建筑形态:‌单层‌,建筑高度‌7.160m‌(未超过8m),体积‌7327m³‌(>5000m³)‌。根据《建筑设计防火规范》(GB50016),丙类厂房需设置室内消火栓系统‌。虽然该厂房净空高度‌7.160m<8m‌,但因其属于‌丙类厂房‌,且体积超过5000m³,仍需按厂房类别执行动压标准‌,动压取值仍为‌0.35MPa‌‌。

QQ君   回复: EHS专家-DL2025-03-28 10:28

谢谢

0    0 [回复]举报

消防资源网 2025-03-28 10:25 00 [回复]举报

消防网友44950 2025-03-28 13:53 00 [回复]举报



7.4.12 室内消火栓栓口压力和消防水枪充实水柱,应符合下列规定:
    1 消火栓栓口动压力不应大于0.50MPa;当大于0.70MPa时必须设置减压装置;
    2 高层建筑、厂房、库房和室内净空高度超过8m的民用建筑等场所,消火栓栓口动压不应小于0.35MPa,且消防水枪充实水柱应按13m计算;其他场所,消火栓栓口动压
不应小于0.25MPa,且消防水枪充实水柱应按10m计算。

关闭

关闭

手机APP下载