消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

GB50016第5.4.2条,经营、存放和使用甲乙类火灾危险性物品的商店、作坊和储藏间,严禁附设在民用建筑内。

厂房内办公区设置的实验室,实验室用石油醚(甲类1项)有机溶剂,设置库房10㎡(一昼夜量),是否违反GB50016第5.4.2条要求。

惊梦 | 2021-09-10 12:12
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

wanqc 2021-09-10 15:23 00 [回复]举报

厂房属于工业建筑,不属于民用建筑,不违反。

厂房内设置中间仓库时,应符合下列规定:     1 甲、乙类中间仓库应靠外墙布置,其储量不宜超过1昼夜的需要量;     2 甲、乙、丙类中间仓库应采用防火墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔;     3 丁、戊类中间仓库应采用耐火极限不低于2.00h的防火隔墙和1.00h的楼板与其他部位分隔;     4 仓库的耐火等级和面积应符合本规范第3.3.2条和第3.3.3条的规定。

关闭

关闭

手机APP下载