排烟设施设置场所问题

关于标准8.5.3和8.5.4中的场所需要设置的排烟设施指的是自然还是机械?比如地上房间大于100平要设置了排烟设施(排烟设置爆款自然和机械),那小于100平是不是自然都不需要了呢?

消防网友52694 | 2022-01-24 11:51
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

消防网友78337 2022-01-24 18:41 00 [回复]举报

排烟设施包括自然排烟设施和机械设施。

如果自然排烟设施的有效开窗面积足够就不需要机械设施,

小于100平方需要有通风窗,无窗房间要按无窗房间的要求进行设置。

刘丽波 2022-01-24 18:50 10 [回复]举报

建规8.5.3条自然与机械均可;8.5.4条除无窗或固定窗的房间外,自然与机械均可;无窗或固定窗的房间采用机械排烟。地上有窗房间大于100平方米,其排烟设施自然机械均可。不大于100平方米的有窗房间不用考虑排烟问题,但其自然通风窗也要满足暖通规范要求,也就是在储烟仓范围内没有开启面积要求。

消防网友52694   回复: 刘丽波2022-01-25 09:04

同理,民用建筑内走道不大于20米是不是也不考虑排烟问题,只需要设置自然通风窗。

0    0 [回复]举报

消防网友34346 2022-01-27 14:20 00 [回复]举报

首先考虑采取自然排烟措施