三级负荷是否在最末一级配电箱处设置自动切换装置?

        建规强条10.1.8 消防控制室、消防水泵房、防烟和排烟风机房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱处设置自动切换装置。

        若是该建筑为三级负荷,要不要设置自动切换装置?

AME | 2022-04-02 19:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

消防网友49953 2022-04-03 18:10 00 [回复]举报

强制性要求,必须要有,问题的争议应该在两路电源的来源问题。

大智无相 2022-04-03 18:59 00 [回复]举报

不用

剑胆琴心 2022-04-06 02:42 00 [回复]举报

设置自动切换装置,两路供电分别来自一路放射式布置的消防供电,另一路引普通用电

中国制造 2022-04-06 09:00 00 [回复]举报

个人理解是,三级针对的是场所或局部,比如某个项目中的一个或几个单体,而不是针对需要设置双路电源的消防设备。

消防网友78337 2022-04-08 18:00 00 [回复]举报

这一问题本身有些问题,有10.1.8相应消防用电设备的建筑,一般综合考虑其建筑规模,其消防配电负荷很难低于二级消防负荷,


所以基本不存在上述问题。

乌伤浪人 2022-04-15 22:24 00 [回复]举报

按规范要求理解,可以不设置。按三级负荷供电的消防设备,其配电箱宜独立设置。我的理解是要专线接入变配电房,以免火灾时被误切断。如果园区内有两个以上变配电间,也可以针对消防泵供电引自两个变配电间,末端双电源自动转换。

知耻也要问 2023-01-06 16:00 00 [回复]举报

自动切换装置 前提条件是 二级负荷,一级负荷的。。 三级负荷不用、

潘天坤 2024-07-02 19:26 00 [回复]举报

建规GB50016没有描述清楚,然后在建筑防火通用规范 GB55037-2022中有明确要求:三级负荷供电的消防用电设备不需要在其配电线路的最末一级配电箱内设置自动切换装置

建筑防火通用规范 GB55037-2022第10.1.6条规定:

除按照三级负荷供电的消防用电设备外,消防控制室、消防水泵房的消防用电设备及消防电梯等的供电,应在其配电线路的最末一级配电箱内设置自动切换装置