仓库内喷淋系统喷水强度按规范选取的问题

仓库危险II级的单双排货架,最大储物高度5米,最大净空高度不超过9米,采用层板通透的钢制货架,喷淋的喷水强度按规范GB50084-2017, 5.0.4条的表格应该是24L/(min*m2)。但如果将货架改为封闭层板或木质货架,按5.0.7条系统设置应按堆垛储物仓库确定,再按表格选取喷淋的喷水强度是16L/(min*m2)。最大储物高度我理解是从货架最上层品物的顶部到地面的距离。

我的问题是:货架由通透层板改为封闭层板,或者改为木质货架,应该是危险性增大了,为什么按堆垛考虑以后,喷水强度反而降低了?不知是不是哪里理解的不对,请专家帮忙解答。非常感谢!



消防网友80558 | 2022-05-28 10:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防网友3475 2023-05-11 10:20 00 [回复]举报

相同最大储物高度,最大净空高度时,货物储存方式不同,火灾蔓延完全不同。在相同的火灾危险等级下,堆垛储物货物之间密切接触,燃烧主要在物品表面延烧;如果是货架存储,燃烧不仅在物品表面延烧,还会因为货架之间的分隔,导致烟囱效应,呈现出立体燃烧的情况,所以货架储物灭火需要的喷水流量、作用面积比堆垛储物大,当隔板采用封闭层板,或者木质货架板时,燃烧时随着木质货架板的塌陷或者封闭层板对烟囱效应的封闭,燃烧路径受阻挡,火灾蔓延反而没有货架存储来得快。