消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

丙类厂房消防水池容积确定

我这个丙类厂房,占地总面积2000平方左右,需要增设室内消防栓系统,水池仅供室内消防栓用水。请问水池容积最低多少能够满足要求呢?

大树119 | 2023-07-05 15:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-07-05 16:03 00 [回复]举报

消防水池的有效容积应根据计算确定,但仅用于室内消火栓的时,最小不能小于50m³


您给出的条件不足,计算需要知道高度和体积,按40l/s(取最大值),丙厂消火栓火灾延续时间3小时,不考虑有效补水的情况下,计算:432m³。设为高位消防水池,有效补水的话,可以按50%布置。


消防给水及消火栓系统技术规范 GB50974-2014

4.3.4  当消防水池采用两路消防供水且在火灾情况下连续补水能满足消防要求时,消防水池的有效容积应根据计算确定,但不应小于100m³,当仅设有消火栓系统时不应小于50m³。



大树119   回复: 安洪全2023-07-05 17:12

谢谢,是单层厂房,应该是按照10升每秒计算,108立方。

0    0 [回复]举报

NailniJ 2023-07-05 16:10 00 [回复]举报

明确项目体量,室内消火栓流量参《消规》3.5.2表;火灾延续时间参《消规》3.6.2表

大树119   回复: NailniJ2023-07-05 17:12

谢谢指教

0    0 [回复]举报

关闭

关闭

手机APP下载