室外消火栓压力

室外消火栓设置有压力要求吗?具体是多少?

柠檬不萌 | 2023-08-31 17:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

同同不同 2023-09-01 08:15 00 [回复]举报

一般情况是地面起算不小于0.1MPa,其他特殊情况参照相关专项规范

安洪全 2023-09-01 08:51 10 [回复]举报

消防设施通用规范 GB55036-2022

3.0.2 低压消防给水系统的系统工作压力应大于或等于0.60MPa。高压和临时高压消防给水系统的系统工作压力应符合下列规定:    

1 对于采用高位消防水池、水塔供水的高压消防给水系统,应为高位消防水池、水塔的最大静压;    

2 对于采用市政给水管网直接供水的高压消防给水系统,应根据市政给水管网的工作压力确定;    

3 对于采用高位消防水箱稳压的临时高压消防给水系统,应为消防水泵零流量时的压力与消防水泵吸水口的最大静压之和;    

4 对于采用稳压泵稳压的临时高压消防给水系统,应为消防水泵零流量时的水压与消防水泵吸水口的最大静压之和、稳压泵在维持消防给水系统压力时的压力两者的较大值。


3.0.3 设置市政消火栓的市政给水管网,平时运行工作压力应大于或等于0.14MPa,应保证市政消火栓用于消防救援时的出水流量大于或等于15L/s,供水压力(从地面算起)大于或等于0.10MPa。


3.0.4 室外消火栓系统应符合下列规定:    

1 室外消火栓的设置间距、室外消火栓与建(构)筑物外墙、外边缘和道路路沿的距离,应满足消防车在消防救援时安全、方便取水和供水的要求;    

2 当室外消火栓系统的室外消防给水引入管设置倒流防止器时,应在该倒流防止器前增设1个室外消火栓;    

3 室外消火栓的流量应满足相应建(构)筑物在火灾延续时间内灭火、控火、冷却和防火分隔的要求;    

4 当室外消火栓直接用于灭火且室外消防给水设计流量大于30L/s时,应采用高压或临时高压消防给水系统。