末端试水装置

请教一下大家,末端试水装置由试水阀,压力表,试水接口组成。那这个试水阀是否和报警阀组的泄水阀是同一个。(就是试水阀是不是就是报警阀组泄水阀)

平心 | 2023-11-11 20:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

阳明心 2023-11-13 08:31 10 [回复]举报

不是同一个,末端试水阀一般安装在系统最远端,有压力表,而报警阀组泄水阀在报警阀组间,没有压力表,两者在功能上有部分一致

37 2023-11-13 09:17 10 [回复]举报

不是

邦哥 2023-11-13 15:05 20 [回复]举报

不是同一个。

1、设置的位置不一样。末端试水装置的试水阀设在喷淋系统的最不利点;报警阀组的泄水阀设置在报警阀间,与报警阀直接相连。

2、作用不一样。设置末端试水装置的试水阀主要为检测系统管路的通畅和系统压力;报警阀组上的泄水阀主要是为检测报警管路时用的。

平心   回复: 邦哥2023-11-18 20:23

请问一下末端的试水阀是不是就是球阀,只是说有两种不同的说法。

0    0 [回复]举报

我的是昵称 2023-11-13 17:09 10 [回复]举报

形式和功能是一样的,都是一个球阀做放水试验的。用途不一样。一个是在湿式自喷的末端,是用来做自喷管网内的压力和水流试验,一个是报警阀放水用的。