消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑的门洞是否可以作为划分防烟分区的措施?

请问各位大佬,建筑的门洞是否可以作为划分防烟分区的措施?

杨阳洋 | 2024-10-08 11:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

磊中 2024-10-08 15:32 00 [回复]举报

你说的太不详细了,什么意思呢?划分防烟分区的措施有挡烟垂壁、大梁、隔墙等等,你这里是一个洞口怎么可能作为划分防烟分区的措施呢?这是连同防烟分区的措施呀

杨阳洋   回复: 磊中2024-10-09 10:29

是想确认门洞上方的那一部分可以不可以看做是防烟分区的分隔措施,我没有表述清楚,不好意思噶

0    0 [回复]举报

LHH2737 2024-10-08 16:27 10 [回复]举报

可以,只要是不燃材料,且高度满足设计要求,不管是什么东西都可以

杨阳洋   回复: LHH27372024-10-09 10:27

了解了,感谢!

0    0 [回复]举报

潘天坤 2024-10-08 17:14 20 [回复]举报

建筑门洞(材质燃烧性能,相关高度等)满足一定条件可以作为防烟分隔的措施,有门的时候就不用考虑高度问题,如果只是门洞的话要满足储烟仓厚度不小于净高10%(当采用机械排烟方式时,储烟仓厚度不应小于空间净高的10%,且不应小于500毫米)或者20%(采用自然排烟方式时,储烟仓的厚度不应小于空间净高的20%,且不应小于500毫米),同时储烟仓底部距地面的高度应大于安全疏散所需的最小清晰高度

杨阳洋   回复: 潘天坤2024-10-09 10:26

感谢感谢!

0    0 [回复]举报

关闭

关闭

手机APP下载