罐区消防灭火设施保温

我公司现有一乙类溶剂罐区,现场配备有移动式泡沫灭火装置,现已进入冬季,最低气温零下20摄氏度,是否可以临近罐区设置蒸汽采暖设施保障移动式泡沫装置不被冻坏,或有其他保障办法?

一生所爱 | 2024-10-23 10:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

喧哗 2024-10-23 17:20 00 [回复]举报

移动式泡沫灭火装置是 泡沫液罐和比例混合器吗?建议放在附近的采暖房间内或者采用电伴热保温包起来

王的MIX4 2024-10-24 14:13 00 [回复]举报

个人感觉是可以的,毕竟理论要联系实际,但是具体还要结合周边环境,储量,采暖系统危险等级,地方规定等多方面确定。一般要求是   储罐与建筑物之间的间距:
● 如果建筑物为一、二级耐火等级,甲、乙类液体储存总量在50t以内,与建筑物的防火间距可为12m;在200t以内,可为15m;在1000t以内,可为20m。
● 容积超过1000m³的储罐或总容量超过5000m³的罐区,与明火或散发火花地点和民用建筑的防火间距不应小于120m,与其他建筑的防火间距应按规定正常值增加25%。
● 位于居民区内的气化站、混气站,其储罐与重要公共建筑和其他民用建筑、道路之间的防火间距,可按现行《城市煤气设计规范》的有关规定执行,但与明火或散发火花地点的防火间距不小于30m。