石化规中装置的室内消火栓系统布置

根据石化规,装置的主要灭火采用室外消火栓及消防水炮。现装置采用花纹钢板楼面,装置中心的设备又不属于特殊危险设备,且各层均无高出楼面15米的平台。烦请问下此类的室内消防系统如何设计?是否需要设置室内消火栓系统或在楼梯间设置半固定式消防给水竖管?谢谢

suixingjie | 2024-10-28 15:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

潘天坤 2024-10-29 12:52 00 [回复]举报

请问是否为甲、乙、丙类厂房(仓库)、高层厂房及高架仓库,或者多层甲、乙类厂房和高层厂房,或者挤压造粒厂房?

甲、乙、丙类厂房(仓库)、高层厂房及高架仓库应在各层设置室内消火栓,当单层厂房长度小于30m时可不设;甲、乙类厂房(仓库)、高层厂房及高架仓库的室内消火栓间距不应超过30m,其他建筑物的室内消火栓间距不应超过50m;多层甲、乙类厂房和高层厂房应在楼梯间设置半固定式消防竖管,各层设置消防水带接口;消防竖管的管径不小于100mm,其接口应设在室外便于操作的地点

挤压造粒厂房的各层应设置室内消火栓,并应配置消防软管卷盘或轻便消防水龙;在楼梯间应设置室内消火栓系统,并在室外设置水泵结合器

  

3211233 2024-10-29 16:12 00 [回复]举报

不属于建筑就不需要设置是室内消火栓系统,且各层均无高出楼面15米的平台,也不需要设置消防竖管。设置灭火器就行。